J James Keller Member Jul 1, 2009 #1 A DC power supply has a 5kw capacity. If the end user maintains control over the output at something less then its rated output, say 3kw, does the NEC allow overcurrent protection sizing based on the 3kw load?
A DC power supply has a 5kw capacity. If the end user maintains control over the output at something less then its rated output, say 3kw, does the NEC allow overcurrent protection sizing based on the 3kw load?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 1, 2009 #2 James, welcome to the forum! :smile: The NEC would never prohibit OCP below a supply's capacity, as long as the rating is capable of carrying the load.
James, welcome to the forum! :smile: The NEC would never prohibit OCP below a supply's capacity, as long as the rating is capable of carrying the load.
Ranch Senior Member Location Global Jul 1, 2009 #3 If a DC supply doesn't have crowbar protection, I don't use it