Strictly speaking if a metal raceway ends up in parallel with the neutral between the utility transformer and the service disconnect you do not have an NEC violation and it happens at every house with RMC between the meter socket and the service disconnect.
I personally have never run, or seen RMC all the way from a service disconnect to the utility transformer.
What I do see is RMC 90s under the service disconnect changing to PVC for the straight run and then turning up at the transformer with RMC 90s again.
Of course we have to bond the RMC 90s at each end which will give the appearance of metal conduits in parallel with the neutral but that really are not. In this case lifting the bond between the RMC and the transformer would be a violation and be dangerous.