E easymoney Member Jul 3, 2009 #1 What kind of readings can I expect if I meg 1/0 5000v cable? what readings would be good, what would be bad.:-?
bob Senior Member Location Alabama Jul 3, 2009 #4 easymoney said: What kind of readings can I expect if I meg 1/0 5000v cable? what readings would be good, what would be bad.:-? Click to expand... Is this a new installaion or existing? How old?
H hardworkingstiff Senior Member Location Wilmington, NC Jul 3, 2009 #5 easymoney said: What kind of readings can I expect if I meg 1/0 5000v cable? what readings would be good, what would be bad.:-? Click to expand... I don't know the answer to your question, but I would love to know what kind of readings you are getting with what equipment.
E easymoney Member Jul 3, 2009 #6 It is a existing installation, not sure of age. They are using a amb-45, and getting around 3500m between each of the three legs at the 500v setting.
electricalperson Senior Member Location massachusetts Jul 3, 2009 #7 you should probably megger 5kv cable at a higher voltage than 500. it should probably be meggered at 5kv-10kv
iwire Moderator Staff member Location Massachusetts Jul 3, 2009 #8 480sparky said: Wow. D?j? vu. Click to expand... Closed, reply to the original