K krlyle1 Member Location new jersey Jul 8, 2009 #1 I saw a inground pool installation we're GFCI breaker was installed for a 220 volt pump motor is this correct ?
I saw a inground pool installation we're GFCI breaker was installed for a 220 volt pump motor is this correct ?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 8, 2009 #2 Yes it's required for a 240 volt pool pump. 680.22(B).
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jul 8, 2009 #4 Remember that before the 2008 code a pool pump that was direct wired was not required to be GFCI protected but it was still okay to install one if one wished.
Remember that before the 2008 code a pool pump that was direct wired was not required to be GFCI protected but it was still okay to install one if one wished.