Can a single-phase electrical panel feeds a 3-pole branch breaker?
You're probably going to have to be more specific. As far as I know, it is possible to physically put a 3-pole breaker in a single pole panel.
Having said that, it probably violates the NEC, it would not be a 3 phase circuit, and it is definitely not a good idea.
If that didn't cover the reason you're asking then give a bit more detail.![]()
Can a three phase panel feed a single phase 2P breaker?
I am just curious...that's all, what section of NEC does not allow it?
Not sure it is specifically covered, because it would be a stupid thing to do. If you have a 1 phase panel, the bus bars distribute power from the two lines of the same voltage; 240V right? So on one side of the panel, they goI am just curious...that's all, what section of NEC does not allow it?
I don't have my code book handy, but seems like their is something prohibiting the use of "delta" breakers in single phase panels.
A delta breaker is not the same as a three pole breaker.
Link to pic and description of a delta breaker.
A delta breaker is not the same as a three pole breaker.
While this statement is true, Hillbilly1 had the right idea. NEC section 408.36(C) Delta Breakers states that "A 3-phase overcurrent device shall NOT be connected to the bus of any panelboard that has less than 3-phase buses."
So the answer is no, you cannot connect a 3 pole circuit breaker to a single phase panel because it would violate the NEC.
Not Correct - A 3-pole breaker is not a "delta breaker" as referenced.
A 3-pole breaker would be within it's ratings - as it would be 120/240V rated.
The listing of the panel should be checked. If the listing only includes references to 1-pole and 2-pole cb's then I would guess that 3-poles would not be allowed. If it only references a circuit breaker type (ie QO) with no reference to the number of poles, then I belive 3-pole would be legal.
Wasasparky, I'm afraid it is you who are incorrect. NEC 408.36(C) states "A 3-phase disconnect or overcurrent device shall not be connected to the bus of any panelboard that has less than 3-phase buses. Delta breakers shall not be installed in panelboards."
This section NEC 408.36(C) prohibits BOTH the installation of Delta breakers in panelboards AND the installation of 3-phase breakers in panelboards that have less than 3-phase buses.
I see your point, but 408.36(C) is titled "Delta Breakers". IMO this section is to apply specifically to delta breakers as titled. Poor wording leads us away from the original intent. If it was a universal rule, then there would be no need to title it "Delta Breakers" - it would simply need to be titled "Three-Phase Breakers"...
Anyone have a single-phase panel handy to see if the number of poles are listed? Otherwise I'll check my panel when I get home...
I can. A Delta breaker is a 3-pole breaker that only receives power from two panel buses. The third pole get's its power from an external input, not unlike a GFCI's neutral terminal, which has no panel main terminal.I don't think anyone could argue that a "3-phase disconnect" and a "delta breaker" are the same thing, so obviously the two sentences are discussing different devices.