ptonsparky
Tom
- EC - retired
We are working on a run of USE wire that tests @.3meg to ground. 1/4 mile plus in length. The other two conductors check out @ 4 - 10 meg with phase to phase about the same. We have found in the past that finding a fault with readings much more than 20k is about impossible, at least with the equiupment I have. Just wondering if anyone has better luck & if so what equuipment you are using.
The USE is 20+ years old and the .3M reading may just be the general condition of this conductor insulation along its entire length. I was there to check out a 75 hp motor that had considerable mice damage & just checked the underground to the pivot for the heck of it.