Relay contact ratings?

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
I was looking to specify a relay to control a 120V branch circuit powering a duplex receptacle, when looking at the maximum load the relay can under it has multiple ratings 1hp @ 120V, 20A ballast, 20A resistive, 1200w tungsten, and 740 pilot duty. My question is what is a ?tungsten? and ?pilot duty??
 

sgunsel

Senior Member
Tungsten means non-inductive loads such as incandescent lighting. I presume(?) pilot duty refers to other relays or contactors, which are inductive and can operate more frequently than motors.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Many people confuse relays and contactors. Relays are usually not rated for very high make (turn on/inrush) and break (turn off/open) ratings, even though their continuous current ratings can be fairly high. Contactors are often rated to make and breaker currents that are many times their continuous current rating (like during motor starting). Rarely do relays exceed 15A continuous while 'definite purpose' contactors are usually never lower than 20A.

If you want to feed a 120V duplex receptacle you really should be using a contactor.
 