imacheezhd
Im wondering if there is a way to determine wire size and ocp if just the size of the unit is known. ie. 2 ton. or if a slide rule is available, or basic chart. Thanks in advance for any help.
Especially without knowing the system voltage and configuration.I don't think it's possible to convert the UOM of output (BTU, tonnage) to an accurate UOM number of input (amps).
So, your constant is 5.625 kva/ton.Ton AC to Amps
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour
4 tons x 12,000=48,000 BTU/hour
48,000/8.533=5,625 watts
5,625/208 volts=27 amps
Have you checked the 208v current on the nameplate of a 1-ton unit?
Hi Larry,
I think 4 tons was implied. (5.625/4= 1.406 kVA) So 27A/4= 6.75A per hr.) But I agree on other factors not mentioned.
Do you walk to school or carry your lunch?Diesel, or unleaded plus?
Do you walk to school or carry your lunch?![]()
Guys, you can't accurately calculate wattage from refrigeration tonnage. A/C units have various SEER ratings. There are several types of compressors; scroll, reciprocation, and rotary. There is no standard efficiency rating on the motors. Some motors are subcooled by the refrigerant. Etc.
Best you can get is a rule of thumb. For single phase, figure 10 amps per ton or 1 hp per ton. (Both are conservative. The actual FLA will be less).
Cooling (BT/Hr)
EER = -------------------------
Electrical input (watts)
or:
Cooling (BTU/Hr)
Electrical input (watts) = ---------------------
EER
then:
Watts
Amps = -------------
Voltage