Hi Guys,
I have a resident who is installing a new meter socket for a single phase 100A service. There is approx. 10' of distance between the meter socket and the main distribution panel (opposite side of the house), so per City Code I had him install a 100A breaker in the meter socket. I also had him land his ground electrode conductors from the water pipe and a ground rod in the meter socket, and had him bond the neutral to ground there, as well. We inspected the service today and found that there is no ground conductor pulled from the meter socket to the main panel. The two phase conductors and neutral between the two are installed in a rigid steel pipe, so I figure that the electrician is relying on the conduit as the path to ground from the panel to the meter socket. FYI - the main panel includes a 100A main breaker.
What do you guys think of this? I know that the conduit is an acceptable means for equipment grounding, so I think that this is OK. But, I want to get other opinions.
Thanks,
Creig
Thanks,
Creig