Old wiring in attic and crawl space

Merry Christmas
Status
Not open for further replies.
There is no NEC requirement that abandonded wiring other than limited energy type of wiring (Phone, class 2 &3 etc..) be removed.

Chris
 
Does it have to be removed if it's not being used? Thank you.
If you are talking about NM cable then, No but I have heard some inspectors make others terminate it in a JB. If it is not connected at either end then it has nothing to do with us. I do try and remove what I can but it is not necessary.
 
I only see the cables listed in sec 820.25 and 830.25 that would have to be removed or identified for future use. Could be a local rule.
 
I only see the cables listed in sec 820.25 and 830.25 that would have to be removed or identified for future use. Could be a local rule.

For other sections for abandoned wiring from the 2008 also take a look at 640.6(C), 645.5(F), 725.25, 760.25, 770.25, 770.154, 800.25, 800.154.