Normally we just run 2-2-4 URD to a detached garage fed with a 100amp breaker to a 22space Main Breaker panel. That covers most needs that a typical garage has (in our area at least).
The garage I'm starting tomorrow, however, has a little apartment in the back section of the garage. Garage footage is 42x36 with the apartment in the last 14 feet (14x36). It has a bedroom, bathroom, and sitting area. The garage will have a 5kw shop heater, there's a 4.5kw water heater, and about 4kw of heat in the apartment area. They also want a 50amp rv receptacle, and a 30 amp rv receptacle (separate from each other).
We're at about 60 amps of just heat (including water heater). Other than what I've already mentioned there will be just general purpose receptacles in garage and apartment area.
I'm thinking we need to go up a bit in feeder size, but not sure how to handle this load calculation. Any feedback would be greatly appreciated.
Sky
The garage I'm starting tomorrow, however, has a little apartment in the back section of the garage. Garage footage is 42x36 with the apartment in the last 14 feet (14x36). It has a bedroom, bathroom, and sitting area. The garage will have a 5kw shop heater, there's a 4.5kw water heater, and about 4kw of heat in the apartment area. They also want a 50amp rv receptacle, and a 30 amp rv receptacle (separate from each other).