Recessed remodel housing in wood
BMacky
Foster City, CA
Anyone know of a mfr that makes a recessed, low-voltage (MR-16 or MR-11) fixture (3" to 4") that has some sort of "air-gap" where the housing makes its way through the wood material of a cabinet, and is listed for such? I see a lot of low-voltage fixtures inside cabinets, not just puck lights, but regular recessed fixtures, cut into cabinet tops for downlighting. I need to do something similar inside a false beam, and have clearance all the way around the can but want to know if the contact with the wood is avoided somehow with a sort of frame that separates the areas of contact with wood. Typical clearances on regular cans I've seen is 2 to 3".
Any takers??
Thank you !
Bob
Bob you need to look at article 410.116(A)(1) or (2)
Here they are
410.116 Clearance and Installation.
(A) Clearance.
(1) Non-Type IC. A recessed luminaire that is not identified for contact with insulation shall have all recessed parts spaced not less than 13 mm (? in.) from combustible materials. The points of support and the trim finishing off the opening in the ceiling or wall surface shall be permitted to be in contact with combustible materials.
(2) Type IC. A recessed luminaire that is identified for contact with insulation, Type IC, shall be permitted to be in contact with combustible materials at recessed parts, points of support, and portions passing through or finishing off the opening in the building structure.
(B) Installation. Thermal insulation shall not be installed above a recessed luminaire or within 75 mm (3 in.) of the recessed luminaire's enclosure, wiring compartment, or ballast unless it is identified for contact with insulation, Type IC.