480sparky

Senior Member
Location
Iowegia
Ungrounded conductors are not listed (although in very specific cases they may be). But overall, for general use, only the grounded (neutral) is addressed in 200.6.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
It's another one of those myths that certain colors are required for certain voltages (other than a high leg).

As the others of said and while it may have been a long held trade practice, the NEC is silent on it.
 

tom baker

First Chief Moderator
Staff member
The NEC does not require any particular color code for feeders, there are certain colors that are restricted in various ways:
White or Gray - Grounded conductor
Orange - high leg delta
Blue - IS systems (Art 504)
Green - Equipment ground

But what the NEC does says is you have to pick colors, post those colors, if there is more than one nominal voltage system:
215.12
(C) Ungrounded Conductors. Where the premises wiring system has feeders supplied from more than one nominal voltage system, each ungrounded conductor of a feeder shall be identified by phase or line and system at all termination, connection, and splice points. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. The method utilized for conductors originating within each feeder panelboard or similar feeder distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each feeder panelboard or similar feeder distribution equipment.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
There is also 517.160(A)(5) which requires Orange, Brown, and Yellow

(5) Conductor Identification. The isolated circuit conductors shall be identified as follows:

(1) Isolated Conductor No. 1Orange with a distinctive colored stripe other than white, green, or gray

(2) Isolated Conductor No. 2Brown with a distinctive colored stripe other than white, green, or gray

For 3-phase systems, the third conductor shall be identified as yellow with a distinctive colored stripe other than white, green, or gray. Where isolated circuit conductors supply 125-volt, single-phase, 15- and 20-ampere receptacles, the striped orange conductor(s) shall be connected to the terminal(s) on the receptacles that are identified in accordance with 200.10(B) for connection to the grounded circuit conductor.

Roger
 

Volta

Senior Member
Location
Columbus, Ohio
It's another one of those myths that certain colors are required for certain voltages (other than a high leg).

As the others of said and while it may have been a long held trade practice, the NEC is silent on it.

It is certainly true that it is not Code. But it was (color codes in general, not different voltages), so the old-timers suffered through it, even though it is gone now :smile:. From at least 1937 until 1968, color codes were required for various branch circuits, depending on multi-wire or not, mostly.
 

480sparky

Senior Member
Location
Iowegia
It is certainly true that it is not Code. But it was (color codes in general, not different voltages), so the old-timers suffered through it, even though it is gone now :smile:. From at least 1937 until 1968, color codes were required for various branch circuits, depending on multi-wire or not, mostly.

Language addressing the colors of ungrounded conductors continued until 1975, which basically stated "Don't use the colors of the grounded or grounding!" Similar language continued until 1996, when the title of Art. 210-5 was "Color Code for Branch Circuits".
 
Last edited:

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
It is certainly true that it is not Code. But it was (color codes in general, not different voltages), so the old-timers suffered through it, even though it is gone now :smile:. From at least 1937 until 1968, color codes were required for various branch circuits, depending on multi-wire or not, mostly.

Well what I was getting at, was believing that B/O/Y with a gray neutral was 277v or the B/R/B with a white neutral was 120V could get you in trouble. It was only a trade practice for years.

And the only one on the site that might remember back to 1937 is Bob.:grin:
 