I just ran across this too.
250.92(B) Electrical continuity at service equipment, service raceways, and service conductor enclosures shall be maintained by one of the following methods:
1. Bonding equipment to the grounded service conductor...
2. Connections using threaded couplings or threaded bosses on enclosures....
3. Threadless couplings and connectors...
4. Other listed devices, such as bonding-type locknuts, bushings, or bushings with bonding jumpers.
So, simply running that 30 foot long bonding jumper in PVC between the trough and the panel doesn't meet the requirements above.... unless we put a "bushing with bonding jumper" into the equation.
Someone early in the thread mentioned that the grounded conductor must be used for the bonding. At that time, I was thinking it wasn't mandatory, just permissible. Now, considering the PVC, it seems to be a requirement.