In article 700.9 (b) requires that you keep emergency and all other wiring independant, than under 701.10 and 702.9 states emergency wiring is permitted in the same raceway with other general wiring. Which is correct is it permitted to install emergency wiring in the same raceway as normal power.
What does the code mean when is says general wiring?
The only places where emergency and normal power is permited in the same location is when you have no other choices. See ecception 1-4
700.9(B) Wiring. Wiring of two or more emergency circuits supplied from the
same source shall be permitted in the same raceway, cable, box, or cabinet. Wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment,
unless otherwise permitted in (1) through (4):
(1)Wiring from the normal power source located in transfer equipment enclosures
(2)Wiring supplied from two sources in exit or emergency luminaires (lighting fixtures)
(3)Wiring from two sources in a common junction box, attached to exit or emergency luminaires (lighting fixtures)
(4)Wiring within a common junction box attached to unit equipment, containing only the branch circuit supplying the unit equipment and the emergency circuit supplied by the unit equipment
IMO General wiring - would be other then emergency - or services