"California Three way's"
Charlie Bob
West Tennessee
I ran into this kind of switch today. Never seen it before.Couldn't figure it out at the moment till i read about it here. Had 4 NM wires to a juntion box , on one they cut the neutral off before entering the juntion box, other two were complete , so to speak, and a fourth wire had the hot one cut off.{ when i said neutral and hot i'm referring to white and black} What do you all think? Do you all usually rewire this? I had to replace the ceiling box they used for junction box. But i debated wether to wire it right or rewire it like it was. What would you all have done? Thanks
CA 3way
CA 3way
Hi Charlie Bob, First up, Welcome to MH's forum. Secondly, I would have rewired the circuit into a dead ended 3-way. rbj
As long as you are phased correctly. And the neutral goes to the light. If every thing is grounded correctly. I don't see any thing wrong with it.
There is only 1 kind of good california 3-way, and let me tell you - it doesnt involve wires.
oh, and just because they work, doesnt make them code compliant. wire it correctly.
~Matt
Is their a code reference for wiring a three way? Just curious.
Not for wiring a 3 way specifically, but there is a code reference that states you have to keep all your circuit wires together. With a Cal 3 way, you are not. I dont know the article off the top of my head - but I am sure someone will add it in.
~Matt
So how about if you fed your switch hot on one side. The switch leg is at the other. Then 14-2 between them for your travlers.
Say you have 4 4way's between them.
If I understand you correctly, you are still splitting the hot and neutral conductors between 2 cables at least once in the circuit - that is not allowed. A diagram would help with this subject.
~Matt
I have pulled many, with out a neutral. Esspecially in conduit, with thhn.
I know this is up for debate, though.
I was just wondering if it is code. I know the neutral needs to go with services , etc...
Well, on circuits not requiring a neutral, 240v - you dont need to pull a neutral. But if the circuit requires a neutral, it has to stay with the other conductors.
An exception would be a switch loop.
~Matt
Yes... several:
200.7(C)(2), 300.3(B) and 404.2.
~Matt
310.4 is Parallel Conductors. :confused:
In the common "california 3-way", also called here "the travelling bus" the continuous hot is on a traveller and in one of the switching states, the common to common conductor is connected in parallel with it. #14 and #12 branch circuit wires are too small to pass muster for 310.4
Like this?