If I understand 225.33 correctly, with the '08 deletion of L&A Panelboards, one could run a 30A feeder to a detached well house and install a 6 circuit panel as the disconnecting means. If there is are two circuits utilized in the 6 ckt panel..say a dp for the well and a sp for a light/receptacle and it is fed by a 30 amp feeder, I see no problem.
Now when taking 225.39 into consideration, if there was a 3rd breaker (say the ligating and receptacle were fed by different branch circuits) would the feeder then have to be a minimum of 60 amp to satisfy 225.39(B) ?
Now when taking 225.39 into consideration, if there was a 3rd breaker (say the ligating and receptacle were fed by different branch circuits) would the feeder then have to be a minimum of 60 amp to satisfy 225.39(B) ?