It is a violation now, it was not always.
good point, Bob. Maybe one day my answers can be as thorough
Yes, in a commercial building, it's a violation.
334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be permitted as follows:
...............................
(2) Exposed in dropped or suspended ceilings in other than one- and two-family and multifamily dwellings
http://www.state.nj.us/dca/codes/code_assist_internet/barrier_free/pdf/sub_3_tech_amend_4_20_091.pdf4. Chapter 3 of the electrical subcode, entitled "Wiring Methods and Materials," is amended as follows:
iii. Section 334.12(A)(2) is deleted in its entirety.
"Everyone want to be Bob." :grin:good point, Bob. Maybe one day my answers can be as thorough
My point is: Where is the line separating existing and new? .............
"Everyone want to be Bob." :grin:
No. Does that follow rules 1 and 2?Have I ever told you about rule 3? :grin:
Bills, Bobs, Berts, whomever.How sad is that?:grin:
I will gladly turn over all my bills.![]()
IMO, if you don't modify it, it is existing.My point is: Where is the line separating existing and new? If the OP's cables in the ceiling can remain as existing (presuming compliant when installed), what about the drop from joist to first fixture? If the old KO plates fit the new fixtures, can the loops stay?
... existing installation ...