GFCI protection of equipment

Status
Not open for further replies.

WKGordon

Member
Does 240.13, if the exceptions are not met, exclude the use of a fusible disconnect on a 480/277 volt service more than 1000 amps? If not, how would you apply it?
 

iwire

Moderator
Staff member
Location
Massachusetts
Does 240.13, if the exceptions are not met, exclude the use of a fusible disconnect on a 480/277 volt service more than 1000 amps? If not, how would you apply it?

You would have to get a fusible switch with shunt trip ability and GFP protection to trip it.

Many of our customers have that set up.
 