Can a panel be used as a splice box? Photo shows conductors entering at the bottom, spliced (left side) and then exiting the top - no connections to the breakers.

With respect to color coding - one splice connects red and white wires together - any problem with that?



IMGP8104_edited-1.jpg
 

480sparky

Senior Member
Location
Iowegia
The white can be spliced onto an ungrounded conductor, see 200.7. In the past, the white conductor was not required to be re-identified. Currently, if this splice is performed today, it would require re-identification.


Only if used in switch loops. If used as an ungrounded (hot) conductor, it was always required to be reidentified.
 

480sparky

Senior Member
Location
Iowegia
...........(note above that there was a mistake in a portion of my second post)

I wouldn't call it a mistake, Pierre. I just think your keyboard doesn't know what your brain does. PEBOAK error (Problem Exists Between Operator And Keyboard). :grin:


To expound on this confusion, using a white wire (technically called grounded today, but back then it was called the identified conductor) in single-pole, 3-way and 4-way switch loops was and is still permitted.

Starting in the 1937 NEC, it was expressly stated that using a white wire in switch loops did not require re-identification as a 'hot' wire, but this exception only applied to switch loops. Using a white as a constant hot wire, such as 10-2 feeding an electric water heater, has always required re-identification at all access points in the circuit (panel, at the heater, any LBs or junction boxes, etc.).

Language was also present that required the white to be used to bring power to the switches, and disallowed it from being used to take the switch leg back to the light.

In 1999, the language changed to require re-identification of the white when used in switch loops.

This concludes todays history lesson.
 