How to derate 4-6 current carrying conductors (CCC) in conduit, 310.15B2a.
This is how I've done it in the past. Say for a 125A load and 4 each THHN CCC.
Conductor Size:
125A X 1.25 continuous load = 156.25A
156.25A/.8 (310.15B2a) = 195.3A from table 310.16 column 90C THHN s/b 2/0 conductors. Some might argue s/b 3/0 because of the .3A over 195A. But knowing 100% of load is not continuous I would go with the 2/0. Check for 75C terminal rating 156.25A < 175A so 2/0 will work.
I'm being told that this is double derating per NEC 210.20a. To size conductors should use actual load of 125A/.8 (310.15B2a) = 156.25A not the continuous load calculated after multipying by 1.25 or the 195.3A for derating. Which would select THHN 1/0 from 90C column. This in effect removes the derating from 310.15b2a for 4-6 CCC and makes no sense to me because this is the way the conductor would be selected with 3 or less CCC.
Conductor Size: