It is most definitely lightning arresters. He is just not seeing the ground...it is there. Having them every 3 poles is a lot.I can only imagine that they are lightning arresters but the bottom of each one would be attached to a pole ground. This seems very strange, photos would be very helpful.![]()
As charlie knows, you would expect them at equipment poles, deadends, corners, risers.
Typical placement is anywhere from every 5th to 10th pole or even 1 or 2 per mile for some areas on some systems. It would be terribly expensive to put them on every 3rd pole throughout the distribution system. They might do this in areas with critical loads or if there have been a lot of direct strikes.