blingbling4r
- Seattle, WA
I was wondering how to size a generator for a fire pump. The code on the required power supply for a fire pump is a little vague as far as the KW rating of the generator except for that it must be "adequate" for supplying the load (fire pump and additional loads). The generator is for backup power as the main source of power for the fire pump will be tapped off the new service that will be feeding the building.
Here are the specs on the 208VAC 40 HP fire pump
FLC is rated at 109A
LRC is 587A
Standby current is 40A
I figured a 600 A for the OCPD is adequate based off of Art 695. I figured the minimum capacity for the generator would be calculated as follows:
[(Fire pump FLC) x 125%] + [(Additional loads) x 100%] = Generator Current
[(208 VAC) x (Generator Current) x (1.73)]/100 = Minimum KVA required to supply the fire pump system
I used the tables from Art 430 to give me a higher FLC based off the HP to give me a little more fudge on the size.
FLC for 40 HP 208V Fire Pump Motor = 114
FLC for 1 HP 208 V Jockey Pump Motor = 4.6
The jockey pump may not even be on the generator system but I added it again for fudge factor.
So to use the formula above I got
114A x 1.25 = 142.5A
4.6A x 1.25 = 5.75A (I factored at 1.25 for safety)
Total Amperage = 148.25 (1/0 THHN wire would be used)
(208 VAC x 148.25 Total Amps x 1.73)/1000 = 53.34 KVA
So I contacted a 3rd party Cummins dealer and got a quote for a 56 KVA generator.
I also contacted the Cummins Direct dealer here in Seattle and when they put the fire pump specs (no jockey pump) through their system they recommended a 112 KVA generator to supply the fire pump. This is a significant difference.
So basically I calculated what it would be for a transformer from Art 695 to figure the minimum supply to the fire pump load. Is this the correct way to do it or is the Cummins rep correct when he "plugged in the numbers" into his application. If so what am I missing here and any code references would be greatly appreciated.
LRC is 587A