120/240 VS 120/208 label/listing.
AZ
New three phase service for sale. It is labeled 800 amps, 120/240 by the MFG.
I assume that the components are the same for 120/208 as for 120/240 but since the MFG label says 120/240, can it be used for 120/208 installation (without taking off the tag:cool:)?
I notice that most stock gear is labeled 250V but occaisionally I see a specific 120/240 or 120/208 tag.
Technical foul?
My bad...service equipment for sale.
A supplier of mine wanted my opinion (for some odd reason) and I told him I'd ask someone who knows.
Me? I'd just make a new label at a trophy shop.
208/240.........whatever it takes
the panel might be specifically for 120/240v 3ph with the high leg, IIRC the bus is constructed so you can't put a 1p breaker on the high leg phase. They cost extra... some areas will allow you to use a 'standard' panel and tag it with 'high leg' or some such wording, but around Chicago some towns are really specific about what panel will be allowed on 240v services.
I do not know of any panel construction that will prevent you from putting a 1-pole breaker into a 3-pole space. however, I have seen panels built with one part of the bus configured and labeled for 3-pole breakers, and another part built and labeled for 1 & 2-pole breakers (the high leg is missing in this part)
FWIW, technically a three phase high leg system should be referred to as 240/120 (I like to include 3P 4W).