- Electrician
I was told that in one bend of a conduit, I couldnt have more than 90 degrees. Meaning an acute angle bend is illegal. I couldnt find anything in the NEC confirming this. Any comments?
What do you consider a U bend?Bending pipe more than 90? is legal, as long as the entire run does not exceed 360?.
In fact, "Shepherd's Hooks" or "Bo-Peeps" are not uncommon.
I have to disagree. More than 90 degrees is illeagal. The code says 4 quarter bends and 91 degrees is more than 1/4 of 360. All of the inspectors in this area would agree with me.
it does not limit the bends to 90 deg.There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.
Ridiculous. What would prevent me from making four 1/4 bends separated by a fraction of an inch?I have to disagree. More than 90 degrees is illeagal. The code says 4 quarter bends and 91 degrees is more than 1/4 of 360. All of the inspectors in this area would agree with me. I've seen them fail jobs where "Shepard Hooks" were used.
Nothing!Ridiculous. What would prevent me from making four 1/4 bends separated by a fraction of an inch?
Or have a very inefficient offset.Nothing!
You would wind up back to where you started...