I thought you could but I am having trouble finding any reference in the NEC that states you can. Is there a code reference?
Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
When sizing for voltage drop, temperature correction or de-rating of THHN, is it permissible to use the ampacity of the THHN in the 90 degree table to get your corrected ampacity?