CT Saturation
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
Anybody have a link to how long a CT can operate without being under load or shorted before a dangerous situation occurs?
Thank you.
electricalperson
massachusetts
I have personally seen an open circuited CT fire up . It was instantaneous .
your smarter than i am :smile:
now that i think about it..isnt the insulaton only rated for a certain amount of voltage? if a CT is open and not shorted you will get thousands of volts so it will probably burn up quickly
SEO
Michigan
Chris are you referring to the meter as the load on the CT's or the building as the load? I'm assuming that your referring to the meter. I've seen the problem happen at a bank where the electrician disconnected the meter from the coils without shorting arcoss them. He was very lucky the POCO was working on a service nearby and disconnected the power. The coil cabinet was buzzing like crazy. I don't know how long it takes to reach a dangerous level but I would think that the more bullding load the quicker it would happen.
brian john
Leesburg, VA
Saw one go in a manner of minutes, the rest I found damaged during service or as part of an emergency call.
The one that blew was left open by the utility after replacement we powered up the service and there was a low pitch wine that went from low to unbearable high pitched as smoke started to fill the electric room. We were running.
chris kennedy
Miami Fla.
The meter as the load. The meter on a 700A 208y/120 CTed service was knocked out of the meter base and hung up in the bent cover. The cover had 2 barrel locks at the bottom so I couldn't get at the shorting bars. The guy running the lift on that side of the building said he didn't do it. If that is fact, it may have been out of the base for a couple days. For this type service POCO would normally supply 300:5 doughnuts.