Paper on the case for MV Data Centers
Paper on the case for MV Data Centers
mull982,
You might be referring to the attached document.
Our VP had me run SKM to check his IEEE 1584 calculations for a comparison between similar 480 and 4160 Volt systems, and credited me as a co-author.
The reason why the MV systems have less Incident Energy (IE) is that the arcing fault current for the MV systems is very close to the short-circuit current so it lets the trip mechanism operate in it's fastest region. Low Voltage arcing faults, on the other hand, are one the order of 1/2 of the value of the short-circuit current, so there's a significant delay that allows for the buildup of IE, often to the 2 second default value.
John M