laketime

Senior Member
If you have two panels side by side one fed from the other. Can you land the neutrals for the sub panel circuits in the main panel?
 
I have seen this done with a two section panel and the neutral bar in only one section.
 
That happens when the small generator panels are used.

I have seen this done with a two section panel and the neutral bar in only one section.
In such a case, the 2nd-panel neutrals have to pass through the same nipple as its feeder conductors.
 
That happens when the small generator panels are used.

In such a case, the 2nd-panel neutrals have to pass through the same nipple as its feeder conductors.


You mean not like this: :roll:

Two%20section%20panel2.jpg
 