From post#2 by megabob:
Outside Feeder Tap of Unlimited Length Rule [240.21(B)(5)
Outside feeder tap conductors can be of unlimited length without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements:
(1) The tap conductors shall be suitably protected from physical damage.
(2) The tap conductors shall terminate at a single circuit breaker or a single set of fuses that limit the load to the ampacity of the conductors. This single overcurrent device shall be permitted to supply any number of additional overcurrent devices on its load side.
(3) The overcurrent device for the tap conductors is an integral part of a disconnecting means or shall be located immediately adjacent thereto.
(4) The disconnect is located at a readily accessible location either outside the building or structure, or nearest the point of entry of the service conductors.
If you met all of the above requirements I think you are compliant.
#4 is always a sticky point and pretty much up to the inspectors interpetation.