230 v motor

Status
Not open for further replies.

mickeyrench

Senior Member
Location
edison, n.j.
Is it a violation of the nec to start a 230v 2 hp sump pump motor with ol protection using just a h.d. 2 pole switch? When are starters required to be used for motors ? I look at 430 and can,t find the infomation i want. Thanks again for help.
 
Is it a violation of the nec to start a 230v 2 hp sump pump motor with ol protection using just a h.d. 2 pole switch? When are starters required to be used for motors ? I look at 430 and can,t find the infomation i want. Thanks again for help.

If the motor has overload protection then no starter is needed.
 
430.2 Definitions.

430.2 Definitions.

430
430.2 Definitions.
Controller. For the purpose of this article, a controller is any switch or device that is normally used to start and stop a motor by making and breaking the motor circuit current.

430.31 General.
Part III specifies overload devices intended to protect motors, motor-control apparatus, ....
(D) One Horsepower or Less, Nonautomatically Started.

430.35 Shunting During Starting Period.
 
Look at 430.109 (C) disconnecting means 2 HP or less and 430.32 (A)(2)
 
Status
Not open for further replies.
Top