taes7t@yahoo.com
Where in the NEC are lighting loads for dwellings and motel rooms defined as noncontinuous?
Thank you.
			Thank you.
Thank you.
It is not defined in the NEC. The NEC give a definition of continuous loads. Generally speaking the dwelling units are not considered continuous
but you and I know that flood lights and kitch lights can be on for more than 3 hours.
"A load where the maximum current is expected to continue 3 hours or more."
I would recommend not filling those circuits to capacity.
IMO if the flood light is on a circuit with other outlets that will not be on for the same 3 hours we do not have a continuous load.
How do I know when a GP branch circuit is full? :grin:
Well if you wire a branch circuit as I do it will usually have all lighting on it. I would then figure the maximum wattage allowed by each fixture. This will give me the max. load.
I agree, but everyone of those fixtures would have to be expected to be on for more then 3 hours at the same time.:smile:
This is a fine line, but all the same, I'm going to have to disagree with the correctness :grin:Correct.
I say this because I ran into this issue at a very expensive estate that some other EC wired. All the kitchen cans, dining room and floods were on the same circuit. Thus when the ho entertained she had all the lights on. The chandelier itself, I believe had about 600 watts. I had her reduce the wattage on the chandelier and the floods since she did not want to run a new circuit.
And if you don't mind, I am going to disagree right back.. . . I'm going to have to disagree with the correctness.
When the code defines continuous load as "A load where the maximum current is expected to continue 3 hours or more", it is referring to the load's current, not the circuit's maximum permitted current.
Exactly what I was attempting to point out :grin:It seems that for my example of 9 non-continuous loads and a 10th continuous load we would count the first 9 at 100% and the 10th at 125% so it is not the entire circuit that is a continuous load.
I agree with the former part of your comment, and cannot give a concise answer on the latter regarding the design stage... in the usage stage I believe the answer is rather obvious. However, I do believe one can make an experience-coupled-with-calculated guess for lighting-only circuits...What Charlie brings up is definitely a wrench in the works and why I asked Dennis how do we know when a GP branch circuit is 'full'?
Riddle me this: If we are allowed to lump general lighting loads (e.g., 3 VA/Ft2) with certain receptacle loads (e.g., 1500 VA laundry circuit), and then we are allowed to reduce the total by applying demand factors after the first 3000 VA, then how exactly are we to insert a 125% factor for the lighting? Indeed, if we needed to add some VA to account for lights being continuous, then why do they let us deduct anything from the total VA (i.e., the total you get by multiplying 3 VA/Ft2 times the square feet)? Why don't they tell us to multiply 3 times the square feet, and then multiply by 125% at that point?
Not my intent. Sorry. I was bringing us back to the original question. In a dwelling unit, we start accounting for lighting by taking 3 va per square foot. Then we get to make the number smaller. My intended message to the OP is that we don't treat that as a continuous load. My reply to your post was a way of backing up my claim that such loads are not to be multiplied by 125%.... but I do believe you are taking the issue way beyond the context of my post :smile:
Correct when calculating feeder and service load, but when considering the number of and loading of required branch circuits we must multiply by 125% for bona fide continuous lighting loads (perhaps even borderline continuous in some cases). This falls under the general requirement for all branch circuits. Consideration as such should in no way be construed to change any Article 220 calculation.
...such loads are not to be multiplied by 125%.
I'm not saying there is no connection... 220 calculations provide the value of minimum required available current on service and feeder conductors serving an area. When dividing that value up into the minimum amount of branch circuits needed to distribute the required available current per 210, we need to consider loads as continuous and non-continuous regardless of the value transposed from 220.So you are implying there is no relationship between 210 and 220, eh? Never the twain shall meet, eh? The one is about picking a large enough service or feeder size, and the other is about installing branch circuits, eh? I have been pushing that agenda for a while now.![]()
210.11 Branch Circuits Required. Branch circuits for
lighting and for appliances, including motor-operated appliances,
shall be provided to supply the loads calculated in
accordance with 220.10. In addition, branch circuits shall
be provided for specific loads not covered by 220.10 where
required elsewhere in this Code and for dwelling unit loads
as specified in 210.11(C).
(A) Number of Branch Circuits. The minimum number
of branch circuits shall be determined from the total calculated
load and the size or rating of the circuits used. In all
installations, the number of circuits shall be sufficient to
supply the load served. In no case shall the load on any
circuit exceed the maximum specified by 220.18.
(B) Load Evenly Proportioned Among Branch Circuits.
Where the load is calculated on the basis of voltamperes/
square meter or volt-amperes/square foot, the wiring
system up to and including the branch-circuit panelboard(s)
shall be provided to serve not less than the calculated
load. This load shall be evenly proportioned among
multioutlet branch circuits within the panelboard(s).
Branch-circuit overcurrent devices and circuits shall be required
to be installed only to serve the connected load.
(C) ***Omitted for brevity
210.19 Conductors? Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity
not less than the maximum load to be served. Where
a branch circuit supplies continuous loads or any combination
of continuous and noncontinuous loads, the minimum
branch-circuit conductor size, before the application of any
adjustment or correction factors, shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
***Remainder omitted for brevity
220.18 Maximum Loads. The total load shall not exceed
the rating of the branch circuit, and it shall not exceed the
maximum loads specified in 220.18(A) through (C) under
the conditions specified therein.
(A) Motor-Operated and Combination Loads. Where a
circuit supplies only motor-operated loads, Article 430 shall
apply. Where a circuit supplies only air-conditioning equipment,
refrigerating equipment, or both, Article 440 shall
apply. For circuits supplying loads consisting of motoroperated
utilization equipment that is fastened in place and
has a motor larger than 1⁄8 hp in combination with other
loads, the total calculated load shall be based on 125 percent
of the largest motor load plus the sum of the other
loads.
(B) Inductive Lighting Loads. For circuits supplying
lighting units that have ballasts, transformers, or autotransformers,
the calculated load shall be based on the total ampere ratings
of such units and not on the total watts of the lamps.
(C) Range Loads. It shall be permissible to apply demand
factors for range loads in accordance with Table 220.55,
including Note 4.