Where are the ground conductors in this photograph? Is there no need for neutrals because it is a 480 V delta feeding only 3 phase motor loads? Perhaps my monitor is causing me some problems but, the smaller wires in the background look like they are marked with gray tape. Please explain cause I'm very grateful that you provided the pic and I'm, now, working a big problem that exists with my ground wires and I'm not sure, yet, where to look.
Whenever current flows in a wire, a magnetic field is produced which surrounds that wire. If the current flow is AC, then the magnetic field will be a continuously changing magnetic field.
Whenever you have a wire in a _changing_ magnetic flux, voltage will be induced in that wire. This includes both the wire that creates the magnetic field in the first place, and other wires nearby. This is the basis of inductance and transformer action. The magnetic field creates the magnetic flux, depending upon the reluctance (magnetic resistance) of the flux path.
When you have the three phases next to each other, the current flowing in each wire is balanced by the current flowing in the other two. The net result is that you get zero net current in the entire bundle of phases. Even though each phase on its own is generating a magnetic field and has inductance, the set of phases together produces only a slight external field and has slight inductance. The larger the space between the conductors, the more magnetic field on the 'outside' of the bunch.
Any ferromagnetic materials in the vicinity will act to 'amplify' the amount of magnetic flux produced by a given current; thus increasing the inductance and the induced voltage caused by any magnetic field.
The 'isolated phase' installation is fine as long as you don't have ferromagnetic rings that enclose the individual phases, and as long as you don't have any conductive loops that are coupled to the magnetic flux produced by the isolated phases.
I believe that the EGC conductors which you added have _caused_ a serious problem. I presume that these EGC conductors are bonded together at both ends of the run. Now consider the following path: start at the EGC junction/termination at one end of the run; now follow the EGC that goes with phase A to the other end of the run. That EGC lands on a junction/termination with all of the other EGCs. Follow the EGC that goes with phase B back to the start of the run. Again this EGC lands at a common termination. What you have is a nice low impedance loop of wire, sitting right in the magnetic field created by the phase conductors.
If the EGC had _zero_ resistance, then the current in each EGC wire would exactly match the current in the corresponding phase. This is because the current induced in the shorted EGC loop will tend to balance the current creating the magnetic field in the first place, thus reducing the magnetic field that induces the voltage in the EGC loop. The actual current flow is set by the balance of phase conductor current, EGC loop current, with the resulting net current producing a magnetic field which produces a voltage that overcomes the resistance of the EGC loop.
-Jon
Thank you for the explanation. I'll disconnect immediately.Whenever current flows in a wire, a magnetic field is produced which surrounds that wire. If the current flow is AC, then the magnetic field will be a continuously changing magnetic field.
Whenever you have a wire in a _changing_ magnetic flux, voltage will be induced in that wire. This includes both the wire that creates the magnetic field in the first place, and other wires nearby. This is the basis of inductance and transformer action. The magnetic field creates the magnetic flux, depending upon the reluctance (magnetic resistance) of the flux path.
When you have the three phases next to each other, the current flowing in each wire is balanced by the current flowing in the other two. The net result is that you get zero net current in the entire bundle of phases. Even though each phase on its own is generating a magnetic field and has inductance, the set of phases together produces only a slight external field and has slight inductance. The larger the space between the conductors, the more magnetic field on the 'outside' of the bunch.
Any ferromagnetic materials in the vicinity will act to 'amplify' the amount of magnetic flux produced by a given current; thus increasing the inductance and the induced voltage caused by any magnetic field.
The 'isolated phase' installation is fine as long as you don't have ferromagnetic rings that enclose the individual phases, and as long as you don't have any conductive loops that are coupled to the magnetic flux produced by the isolated phases.
I believe that the EGC conductors which you added have _caused_ a serious problem. I presume that these EGC conductors are bonded together at both ends of the run. Now consider the following path: start at the EGC junction/termination at one end of the run; now follow the EGC that goes with phase A to the other end of the run. That EGC lands on a junction/termination with all of the other EGCs. Follow the EGC that goes with phase B back to the start of the run. Again this EGC lands at a common termination. What you have is a nice low impedance loop of wire, sitting right in the magnetic field created by the phase conductors.
If the EGC had _zero_ resistance, then the current in each EGC wire would exactly match the current in the corresponding phase. This is because the current induced in the shorted EGC loop will tend to balance the current creating the magnetic field in the first place, thus reducing the magnetic field that induces the voltage in the EGC loop. The actual current flow is set by the balance of phase conductor current, EGC loop current, with the resulting net current producing a magnetic field which produces a voltage that overcomes the resistance of the EGC loop.
-Jon
Thank you for the explanation. I'll disconnect immediately.
I don't know if there is an acceptable method of adding an EGC to an isolated phase installation.
If you had an isolated phase installation that required an EGC a full size EGC would have to be included in each raceway.
Sounds logical to me.
steve
I guess we are both dumb 'cause I was wondering the same thing. Very seriously, though, it was my plan to leave only one of the egc's remaining and the neutral pipe is the only choice I seem to have. According to table 250.122 the size should be 1/0 for my 800 A main. Perhaps we can talk about the nature of the EGC being colocated with the iso phases. What purpose does the EGC serve for each of those phases if any? I'm having trouble seeing in the code and electrically how locating the EGC outside of the isophase pipes is a violation or a life safety issue. Anybody?That is what I thought.
But if you have an EGC in each raceway, and have all of the EGCs connected in parallel as was done here, then you will have undesired current induced in the EGCs.
Dumb question: Do all of these full size EGCs need to be joined together at _both_ ends, or could an EGC be placed in each conduit but only one actually connected at the downstream end?
-Jon