What is yhe demand for a 5kW cooktop and a 9kW wall mounted oven?

I used column C and combined the two values for a total of 14kW. Then used note 1 and came up with 8.8kW. Is this the correct way to do this?

Thanks
Kevin
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What is yhe demand for a 5kW cooktop and a 9kW wall mounted oven?

I used column C and combined the two values for a total of 14kW. Then used note 1 and came up with 8.8kW. Is this the correct way to do this?

Thanks
Kevin

That's the way I would do it.

Note 4 last sentence gets you 14kw. Col. C has 8kw for 1 range rated 12 kw and then we need to add the demand for the extra 2 kw (Note 1)at 5% for each. 10% of 80= .8 thus we have 8 + .8= 8.8kw.
 