welcome to the forum.
it really depends on if the control wires are class 2 or 3 circuits. Take a look at 300.3(c) and 725.136(a) for class 2 and 3 circuits.
Another question is this generator supplying emergency loads?
Chris
I ran into this situation about a year ago. The Generac packaged units (the ones that are pre-engineered and come with their own xfer switch) come with a 30' whip in an armored jacket. Inside the jacket are the generator power wires (sized accordingly), a ground and 4# 16 control wires with a Molex connector on the generator end. I had to extend the generator circuit beyond 30' and was told by the local rep that I could not make up my own whip because if the control wiring wrapped itself around the generator power wires the induction produced by the power wires could damage the transfer switch. I didn't question why, I just ran the end of the whip into a 6 x 6 JB and extended the power & control circuits another 20' by using 6/3 MC and a run of 14/4 AC. Worked fine and never had any call backs.LarryFine said:Generac seems to have no problem with running 240vac and 12vdc in the same raceway.
Some manufactures will not warrant the unit if say, you run the charger,or blockheater circuits in the same conduit as the start control, even though you use 600 volt wire for all conducters. I've been told by Kohler that they will not warrant it.
Show me some paper work!
We see it done all the time, personally I would not do it. But if the insulation class is rated for it there should be no issues.
I have not seen any paperwork stating this, but have had several startup techs with Kohler say they will not sign off if the control wiring is in the same conduit as the 120.
I was just connecting an 80 KW Genrac on Wed and Thur.
JUNK absolute the worst piece of junk that I have had the displeasure of wiring.
Give me a CAT or a Volvo, or Onan / Cummings but the Generacs should be used for mooring anchors.
I have hooked up many Generac, and I have seen the ones that come with the prewired panel with the FMC have the DC control wires in it from the factory, but what confuses me, is when you have the stand alone whole house transfer switch the instructions in the installation book (yea I read it once) clearly states to run them in a separate wiring method, N1/192, N2/193 utility sense wires can be run in the same conduit as they are just the 240 volt taps to the utility side of the TS, but 15, 15A, 23, can't remember the other number, is the 12 volt DC control and has to be in another race way or cable as per instructions.
So I guess if they do it it's ok but if we do it it's not![]()