Bond Screw on Old Style QO Panel
Sparky555
I have a work order to remove the bond screw on an old style 100 amp Square D QO panel with the neutral bar horizontally above the main breaker. I can't figure out which screw it is...help. Please don't sat it's the green one. They're all the same color.
I had to remove factory installed bond straps (brand new panels this year) on 5 floors of Siemens 277/480 volt 225 amp MLO panelboards, they did not use green screws either, but was bolted solidly to the neutral bar and the panel can. Found them when doing megger test on feeders before energizing panels. Could be the same on the Square D, may be a strap instead of a screw.
It's the one screwed thru to the can :rolleyes:
Seriously, just look at it and it will be obvious. One pair of screws will hold the inslated "stand off" in place and the terminals themselves will be evident.
Makes sense. I was hoping someone knew right, center or left. I probably need to put more light on the subject.
Thanks.
tell them it was up to code when installed
I think some of the older SQ D panels didnt have bond screws. The neutral was part of the breaker assemply that bolted onto the can. If this is the case tell the home inspector or realtor that the panel was manufactured that way and cant be altered. Use the UL listed reason, OR move all the neutrals to a seperate buss bar that is listed for the panel (there wont be any).
Do you have the right address? :grin: Not that I ever repaired the wrong grain dryer or anything like that.
You gotta hate that! One of our guys changed a service on the wrong house. The homeowner came home to find the electrician in his house working on it and was :mad::mad:. Doh!
The right house was next door...
I imagine, that, by the time you read my post, you'll have closely examined the neutral bar. I installed a lot of these little 20 pole panels, back when. The main bonding jumper screw, in this panel is a round head machine bolt, about 1.5" long, that is snugged down tight to the face of the neutral bar.
You're right that it is the same color as the other screws. The neutral terminal screws have more "cylindrical" heads, and will be up from the face of the bar, unless they have been so overtightened as to crush the conductors. Also, in this vintage, many, if not all, of the neutral bar terminal screws had a little thin U-shaped metal clip below the head and inserted into the conductor hole -- the bond screw isn't like that.
Ivesnroute's suggestion about the label showing the location is an excellent one. Hope the label hasn't fallen off.
Look inside the panel on one of the sides for a label. There should be a 'diagram 1' and a 'diagram 2'. In 'diagram 2' you will find a drawing with the location of the screw which should be the center screw in the center bar.
That is if it's like the one I just worked on.
You nailed it. Round head, dead center under the large lug. Thanks to all.
Also, in this vintage, many, if not all, of the neutral bar terminal screws had a little thin U-shaped metal clip below the head and inserted into the conductor hole.
Yea, what's up with the little metal clip?:smile:
I've encountered more than a few of those.
Sure makes it aggravating to get a wire into the terminal.....especially if the panel is (as usual) crammed full of wires.
Stranded wire?
I did a service change where the POCO cut the overhead drop on the wrong house.
I was standing in the back yard, waiting for him to drive down the alley, and I see the power lines swaying. He cut the drop about 4 houses away.:roll:
That was the way SqD took an older terminal bar and improved the "listing" to include stranded conductors. They eventually improved the entire terminal bar and no longer needed the little metal clip.
This "little metal clip" was from an era when stranded small gage branch circuit conductors were starting to appear at, or just a little more than, the price point that solid conductors were. Installers were finding the labor savings of stranded #14 & #12 attractive enough that the way the old SqD neutral bar screw cut the strands was dealt with.