dschultz307
I am in need of advice on the following scenario:
UPS battery plant has failed and UPS cannot carry critical load during an outage/transfer to secondary feeder or generator.
It will be at least a week until new UPS batteries are installed.
Mission critical facility.
Double ended switchgear (two feeds w/tie breaker; two generators, only one allowed to run at a time)
Facility less than six years old, about 100 hours on generator
Opinions on the following actions:
Leave it alone---The commercial power is more reliable than the generator.
Switchgear controller in AUTO, Turn off commercial feeds, allow switch gear to select one generator, transfer to other if a failure occurs.
Switchgear in MANUAL, Power facility on one generator.
I understand that a transfer to generator would result in a critical load outage under any circumstance.
Thanks,
Dave
Thanks,
Dave