I realize that a grounded conductor cannot be landed in a panelboard or switch within a terminal that is already taked by another conductor unless the terminal is listed for that application or is run in parallel. My question is I cannot find where the code says that the grounding conductor has to land on an idividual terminal-lug and cannot be grouped with another grounding conductor. Can anyone assist.
 

benaround

Senior Member
Location
Arizona
I realize that a grounded conductor cannot be landed in a panelboard or switch within a terminal that is already taked by another conductor unless the terminal is listed for that application or is run in parallel. My question is I cannot find where the code says that the grounding conductor has to land on an idividual terminal-lug and cannot be grouped with another grounding conductor. Can anyone assist.

As far as the code goes, it is under 110.3(B) following the manafactures instructions. There

are lugs that are good for 1 conductor, and others that are good for more, it will say so

right on the lug.
 