E ELECTRICAL SYSTEM'S Member Aug 12, 2009 #1 Does a Water fountain and or Water cooler have to be GFI protected?
mistabass Member Location Rhode Island Aug 12, 2009 #2 fountains 680.51 water cooler422.52 yes on both
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 12, 2009 #3 depending on the Code cycle enforced,.,, 410.52 was added in '08 NEC
S SEO Senior Member Location Michigan Aug 12, 2009 #4 Section 422.52 is new in the 2008 NEC. If you are on the 2005 NEC look at section 210.8 (A) & (B) for receptacle requirements for cord and plug connected coolers.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 12, 2009 #5 error on my post..too late to edit 422.52
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 12, 2009 #6 Where's the requirement for water coolers? 422.52 is for drinking fountains not water coolers.
mistabass Member Location Rhode Island Aug 12, 2009 #7 my bad sorry infinity thats what i call drinking fountain/ bubbler
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 12, 2009 #8 mistabass said: my bad sorry infinity thats what i call drinking fountain/ bubbler Click to expand... No problem, there were multiple posts saying the same thing. I was just trying to find the requirement.