History of Grounding
tom baker
Bremerton, Washington
Master Electrician
I am working on a brief history of significant changes to grounding
Here is what I have so far
1923 NEC - First mention of driven rod or pipe electrodes
1925 NEC - Driven rod electrodes now called ?artificial?, 8 ft long, 1/2? rod or ?? pipe
If resistance >25 ohms, requires 2 electrodes spaced 6 feet apart
1951 NEC - Ten feet of less of metal water pipe must be supplemented with additional electrode
1947 - Grounding receptacles required for laundry
1956 - Grounding receptacles required for garages, basements, outdoors
1962 - All branch circuits must include a grounding conductor
16 AWG for 12 and 14 gage circuits, 14 AWG for 10 gage circuits
1963 - Research paper presented by H.G. Ufer at IEEE Conference
1969 - Full size ground required for circuits
1971 - Water pipe electrode must be supplemented with additional electrode
1971 - Ufer ground must be used ?If Available?
1974 - NFPA TIA ?if available? does not mean it has to be used.
1999 - Additional electrode must have resistance of 25 ohms or less, or be supplemented with additional electrode
1993 - Interior metal water piping more than 5 ft from point of entrance can not be used as part of the grounding electrode system
1999? - No longer allowed to use use neutral for frames of ranges, etc
2002 - Can't reground neutral if creates a parallel path to separate buildings
2005 - Ufer ground must be used when present
2005 - Bonding added to title
2008 ? Supplementary ground rod changed to auxiliary ground rod
2008 - Ground is now the earth
2008 - Can not reground the neutral at separate buildings
Need to know: when structural steel/metal was added
When was bonding added, my 1956 NEC doesn't mention
And the above may not be 100% accurate. I don't have code books before 1968
Do you have an Article number for the years around that area you are searching in?
Tom, check out Antique's site here. Lots of old code books free for the browsing. I am sure that ground rods and water pipes were mentioned prior to 1923, they were called lightning arresters (for example, page 32 of 1915).
The first edition of the code to contain the 25-ohm section was the 1918 edition. Also in the 1918 edition, the first allowance for pipe electrodes became code. The original requirement permitted a minimum of a 1-in pipe with no less than 4-ft? of surface to exterior soil. The 1923 edition added the driven rod.