- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
I have a similar question to this, but I didn't want to threadjack him.
I am replacing old services and panels, formerly FPE. Since the FPE has such a great reputation for not tripping under faults and overloads, I decided it would be a good idea to megger all the aluminum feeders, between the services and the interior panels to see if the feeders needed replacement.
In my searching, I am familiar with the 1 Megaohm rule of thumb, but these feeders are all over the boards, and nowhere near 1 megaohm, they're well over that. The lowest I've seen so far is over 100 megaohms, IIRC. Am I just lucky, or am I not being picky enough? The copper feeders I installed yesterday instantly maxed out beyond 11 gigaohms, which got me thinking maybe I'm not being picky enough.
I am just testing each ungrounded conductor to the EGCs, with the breakers in the panels off, to test the feeder.
1. What would your minimum resistance be to recommend replacing the feeder?
2. Should I go ahead and test between ungrounded conductors too? Ungrounded to grounded? I figured the most glaring result would be from ungrounded to EGC.
All comments welcome, thanks.
I am replacing old services and panels, formerly FPE. Since the FPE has such a great reputation for not tripping under faults and overloads, I decided it would be a good idea to megger all the aluminum feeders, between the services and the interior panels to see if the feeders needed replacement.
In my searching, I am familiar with the 1 Megaohm rule of thumb, but these feeders are all over the boards, and nowhere near 1 megaohm, they're well over that. The lowest I've seen so far is over 100 megaohms, IIRC. Am I just lucky, or am I not being picky enough? The copper feeders I installed yesterday instantly maxed out beyond 11 gigaohms, which got me thinking maybe I'm not being picky enough.
I am just testing each ungrounded conductor to the EGCs, with the breakers in the panels off, to test the feeder.
1. What would your minimum resistance be to recommend replacing the feeder?
2. Should I go ahead and test between ungrounded conductors too? Ungrounded to grounded? I figured the most glaring result would be from ungrounded to EGC.
All comments welcome, thanks.