ballast failure question
Mt. Airy, MD
I'm having ongoing issues with premature electronic ballast failure in HID fixtures. The fixtures are pendant-style, 120VAC, 150W MH, with the ballast in a cylindrical housing directly above the lamp. These fixtures are suspended from a 22' ceiling in a retail store, the bottom of the fixture about 14' off the floor and the ballasts about 18' off the floor. The ballasts last approximately a year and then burn out.
We have determined that there is no incompatibility between the ballasts and the lamps. The ballast manufacturer ran lab tests on the last batch of failed ballasts and came back with failure due to shorting to ground. There is no issue with miswiring of the ballasts nor has there been, nor is there any evidence in the fixtures of arcing or shorted anything. No breakers tripped, nothing burned, discolored or smelling odd in the fixtures.
The fixture manufacturer and the ballast manufacturer are now trying to figure out if there is any incompatibility between the fixtures and ballasts. I am going to put these lamps on a regular replacement schedule so they are swapped out after approximately 80% of their estimated life, rather than waiting until they burn out, because I believe old lamps stress the ballasts and can contribute to their early failure.
Heat may be a contributing factor as well. The ceiling is high, the area where the lamps hang is small, the ceiling and fixtures are painted flat black, there are numerous obstacles to free circulation of air at ballast level (e.g. HVAC ducting, none of which blows cool air on the ballasts, it is well below their level), the heat from the lamps goes directly up into the ballasts, and the ballasts tend to fail in hotter weather. I took temperature readings on the ballast housings in early morning on an overcast day, and it was about 5 degrees F warmer on the housings than it was at chest level from the floor.
What I need to ask is, has anyone out there encountered a similar situation, and what did they find as some possible causes for the problem? Any ideas would be welcome. Thanks.
Thanks Bobhook...duly noted and appreciated. However these lights are not on 24/7 but roughly 10 hours a day, it is a retail store and they turn the lights off when they close. The lamps aren't failing prematurely, just the ballasts. I have had no lamps blowing up in this application (thankfully!).
Heat is definitely the problem you're having. Electronic ballasts in particular are VERY sensitive to excessive heat build-up.
Were the fixtures supplied from the mfgr. painted black? If not then you will find yourself up a creek as field painting them can and most likely will void the warranty.
You need to find a way to get some of that HVAC air on the ceiling to cool things down. It would be worthwhile to talk to the HVAC contractor who installed the system to see what if anything can be done. Could be as simple as making ceiling-level return air intakes to help move some of the heat.
Another thing that may help if you can find someone to make a finned aluminum wrap for the ballast assemblies to add some surface area to get rid of the heat.
My first suspect will be heat..one other thing i would like to check is the voltage available at the lamp itself. (is the voltage dropping?)..
If the ballast is totally enclosed then there is build up of heat..the suppliers should be able to give solution to this....(use a perforated cover..etc..)
You may also check for voltage spikes/dips by connecting a powermeter for 24 hours..
cheers.