Selective coordination is made easier to achieve if you eliminate the instantaneous part of the TCC curve. This can be done because switchgear has been tested to withstand its fault current for a longer period of time (30 cycle) as compared to switchboard construction (3 cycle).
If there is not much redundancy in the quantity of gens, you might want to leave the instantaneous on for the generator breakers anyway to protect the generators from feeding into a fault for long periods of time and damaging the windings.
SWBD construction requires the instantaneous to be on all the time.
Search the internet for selective coordination.