Cow
- Eastern Oregon
- Electrician
Picked up a work order this morning to check a tripping breaker at a residence. I show up and it's a fifth wheel travel trailer with the problem. I usually tell folks we don't work on RV's but figured since it took 10 min. to drive out here, I'll do a little investigating to get my min. 1 hr charge.(I really hate taking 15 min. to drive out somewhere, just to show up and tell them we don't work on that. I have a hard time charging our min. hour, since I feel our office guy should of caught it.)
Anyways, you could see the floor had been wet right in front of the kitchen sink. Threw the offending breaker on just for giggles, tripped immediately. Pulled out the Fluke 1507, pulled the wires off the breaker and neutral bar, megged the hot-grd, neut-grd, zero. Dead short. I wasn't entirely sure what all was not working and what was, this trailer had about 20 different lights with 20 different switches scattered all over the place, I just decided to get out the circuit tracer and follow it. Here's another plug for the Amprobe 2005(Quogue would be proud!
). Started tracing from the panel across the cieling, down the wall through a recep to under the floor and over to the kitchen. It was headed right to the wet floor area, traced it to an access compartment in the toe kick of the cupboards. Low and behold, 4 romexes coming from the belly of the trailer had the sheath chewed on from the floor line up to about 3 inches, plus they were wet. Couldn't get any slack in the wires to splice them and couldn't figure out how to get access to repull the cables, so I had the customer call a trailer repair outfit.
Hey, at least I found the problem for you?:grin:
I was just curious who else does this type of stuff when you show up and it's not what you expected?