doctors office exam room in slab roughin
bcarol67
i failed an inspection for exan rm. in slab rough I used pvc boxes and pipe. the inspector says only metal boxes and rigid is allowed in exam rooms. I cannot find it in the code book. Please help.
Welcome to the forum. Your answer is 517.13(A) He is wrong about only RMC being allowed though.
Roger
Take a look at 517.13
(sorry Roger. I had to look it up..you probably did it from memory :) )
but at least we agreed
Gus, we are on the same page.
Roger
thank you for your help but look at 517-13b methods
517.13(B) (BTW what year NEC are you using?) is in addition to 517.13(A), it doesn't relieve the requirements of 517.13(A)
517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
Roger
exam rm.
exam rm.
i wasnt there to meet the inspector but thanks for all the help. looks like ill be replacing the pvc.