277v lighting vs. 120v lighting
Jeff80
Why is 277 lighting more efficient and save money? Dont they draw the same watts? Is it just heat loss saved because of the low amp high voltage aspect?
peter d
New England
Watts are watts. The voltage is not relevant.
The greatest benefit to using 277 volt lighting is that you can put a lot more ballasts/fixtures on a circuit than 120 volt circuits. Voltage drop is less of a concern as well.
drbond24
They do use the same amount of power (watts), but if the voltage is higher then the current is lower to get that same power. Lower current means less losses on the systems and more fixtures per circuit.
Pretty much what you already said. :)
Mr. Bill
Michigan
Watts are watts as others have stated. This is just one of those myths that continues. It's more of a material savings to connect lights at 277V.
If something just doesn't sound right to you it's always better to verify the information before speading it to others.
augie47
Tennessee
That would shut the Forum down :grin:
folks like myself couldn't post:)
broadgage
London, England
Presuming that we talking about flourescent or discharge lighting with electronic ballasts, then 277 volt operation is very slightly more efficient.
All such ballasts use DC internally, with the incoming supply being rectified.
The losses in the rectifier are the product of a fixed voltage, about 1.6 volts, and the line current, which is less at 277 volts.
Consider a ballast with a current draw of 1 amp at 120 volts and a voltage drop in the rectifier of 1.6 volts, this is clearly a loss of 1.6 watts.
Now connect the same ballast to a 277 volt supply, and it will draw about 0.4 amp, the voltage drop in the rectifier is still 1.6 volts, giving a watts loss of about 0.64 of a watt, and saving about one watt.
Therefore there is a saving but it is very small.
The watts input to a ballast is normally only stated to the nearest whole watt, therefore on small ballasts the tiny saving is hidden.
For example a ballast that uses 29.8 watts on 277 volts, and 30.1 watts on 120 volts, would be described as "30 watts" on either voltage.
If the building has 277/480 volt service with 120 volts being obtained from a transformer, then working lighting at 277 volts will avoid the losses of a few % in the transformer in addition.
On a new install, the transformer would be smaller and therefore cheaper in addition.
However as others post, the biggest saving is on time and material.
Many more lamps can be installed on a 277 volt circuit, compared to a 120 volt circuit.
In many cases a smaller wire size can be used.
Code requires a minimum of #12 on a 20 amp circuit, however in practice on a 120 volt lighting circuit, #10 or even #8 may be required in order to avoid excessive voltage drop. (unless the circuit is very short)
At 277 volts, the minimum wire size permitted by code will often suffice.
Although the NEC does not place any exact limit on voltage drop, 3% is often regarded as acceptable.
3% of 120 volt is of course 3.6 volts.
3% of 277 volts is about 8.3 volts.
Therefore a 277 volt 20 amp circuit can be well over twice as long as a 120 volt 20 amp circuit, before voltage drop requires larger conductors.
hurk27
To add to the others, voltage drop is not only the running current of the lamps after they have struck an arc, but inrush when first turned on, which can be much higher. this can cause HID lights to fail to strike an arc.
I have seen this more on 120 volt fed HID lighting than at higher voltages.
