KVA to watts

Status
Not open for further replies.

drbond24

Senior Member
I have a MAU with a dry type transformer that is rated at 2 KVA. How many watts is two KVA?

It would be helpful to know why you are asking as well. If you are wanting to figure the wire size for feeding the transformer, for instance, you want to use the kVA and not the Watts. If you just want to make sure the transformer is large enough to supply a load of 2000 W, it will. If you are wanting something totally different then tell us and we'll be more helpful (hopefully). :)
 
Last edited:
Status