Calc Neutral Current

Calc Neutral Current

For calculating the Neutral load on a 120/240 3 phase service am i allowed to use the 70% demand factor.

This may be off the subject a little,
just passing it along because it is so neat.

*:) EL_IneutralCurrent_equation.txt
Ineutral =
SQRT (
I?A + I?B + I?C
- (IA x IB) - (IB x IC) - (IC x IA)
)


:)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
This may be off the subject a little,
just passing it along because it is so neat.

*:) EL_IneutralCurrent_equation.txt
Ineutral =
SQRT (
I?A + I?B + I?C
- (IA x IB) - (IB x IC) - (IC x IA)
)


:)
That would not apply to a 120/240 volt 3 phase system.
 