Hi,
It is our understanding that if more than one inverter is part of a PV system, then the breakers for those inverters have to be in a (separate) sub-panel. Please let me know if this is correct.
The situation we have is a 400am main service with a breaker panel attached, there is a separate breaker panel connected to a breaker in the main service panel. My question is "could we put one inverter into each breaker panel or do we have to install a new separate sub-panel?" The inverters are SMA 6000US which have a max continous AC current of 25 amps, times 1.25 = 31.25 amps so I need 40 amp breakers for each inverter. 80 amps is within the max backfeed of the main service.
Photo attached of panels
Thanks
David
It is our understanding that if more than one inverter is part of a PV system, then the breakers for those inverters have to be in a (separate) sub-panel. Please let me know if this is correct.
The situation we have is a 400am main service with a breaker panel attached, there is a separate breaker panel connected to a breaker in the main service panel. My question is "could we put one inverter into each breaker panel or do we have to install a new separate sub-panel?" The inverters are SMA 6000US which have a max continous AC current of 25 amps, times 1.25 = 31.25 amps so I need 40 amp breakers for each inverter. 80 amps is within the max backfeed of the main service.