Tapping off of disconnect?

Status
Not open for further replies.

ItsHot

Senior Member
Can a new device be fed from tapping off of a disconnect? For example..exsisting 50 A ciruit with disconnect, can a new 20A circuit be tapped out of the disconnect? Searching for art. in NEC.:confused::)
 
The tap rules for branch circuits can be found in section 240.21(A) which refers you back to 210.19.

In general, the scenerio you describe is not permitted.
 